Peplink 580 Temperature

Hi
I have peplink 580 load balancer and i just updated the firmware to 7.1.1 build 2460.
I just need to know if the Temperature of the device is normal.
here is what I found on the dashboard:

Temperature: 51.5 °C / 124.7 °F

Thanks

The temp will depend on several factors. What location is the 580 installed in? Is it a closed rack, an open rack, does it have other devices installed around it? Does the room have AC?

1 Like

What location is the 580 installed in? Is it a closed rack, an open rack?
Its in a closed rack
does it have other devices installed around it?
yes . above it is a cisco switch only.
Does the room have AC?
yes. the AC is set to 18 so the room is cold.

@waheeb

Please refer to the following forum post. That should explained your concerns.

1 Like

Ahaaaaah, Then its normal :grinning:.
Thank you

Hi again,
the temperature exceeds 60.0 °C, is it OK?

I also need to know the temperature limits (min value, max value).

Its an intel processor in the B580 I think, so anything under 100 °C and you’ll be fine, although if it runs consistently above 70°C then personally I’d add airflow / cooling.

1 Like

I’m having these reads(up 56) only when the AC is OFF.

Thanks a lot